![]() |
mansard roof and mwfrs
mansard roof and mwfrs
how do others handle windloads for a large flat roof structures with a steep slope mansard roof around the perimeter? using asce7 low-rise building, the steep slope will significantly increase the mwfrs wall pressures compared to a flat roof. it doesn't make sense that adding a mansard roof above a 3rd or 4th floor should increase the wall pressures at the 1st floor. check out our whitepaper library. well you don't say which version of asce-7 you are using so i'm going to answer based on 7-98 since i have that edition in front of me. i would assume a similar answer for more recent editions. 7-98 has 2 figures to address mwfrs pressures, 6-3 and 6-4. since you state 'low rise buildings' i'm assuming you are using something similar to figure 6-4 which is for h<60. from what i've heard, this figure was developed based on requests from the metal building association in order to reduce their loads, notice the table title states walls & gable roof (and thats what the pictures show) since that is what metal buildings typically look like. if you have a steep mansard around the perimeter of a multi-story building, i would think fig 6-4 may not be the best figure to use. if you use figure 6-3, notice the wall pressure table does not take into account roof pitch or corner zones. this is a more general table (albeit more conservative for some structures) that can be used for most buildings. |
所有的时间均为北京时间。 现在的时间是 11:26 PM. |