field welded moment connections-ibc
field welded moment connections-ibc
could someone explain their understanding of the construction requirements of a field welded moment connection for a omf in seismic site class d between a beam flange and column flange? specifically, how are the welds supposed to be run out/ground off at their ends to eliminate stress risers. also, i have been told that the bottom backer bar has to be removed, the weld back gouged and a 5/16 fillet placed over the original weld. is this requirement only for a omf? only in class d? why is the bottom weld different then the top weld? any thoughts would be appreciated. jtpe: with regards to the run-off tabs, please refer to fema 353, 4.2. the 5/16" fillet is the reinforcing fillet weld noted in d1.1, figure 3.4 (tc-u4a-gf), note 7. i recommend getting your hands on copies of fema 350 - 353. |