double ceiling beam
double ceiling beam
can anyone give me a reference for lateral stability of unbraced ceiling beams? i have two horizontal beams with king posts @ the one third points. i plan on spacing the beams 3 1/2" apart and providing a spacer block sandwiched between the clg beams below the king posts. spacer block will be bolted thru the clg beams with an all-thread. beam stability, cl is controled by lateral support, not bearing. without lateral support or proper design considerations, the compression side of a beam may buckle prematurely at a load much smaller than what was intended in a normal bending mode. but, the height to thickness ratio of typical wood headers (2-2"x12" or 2"x10"), 3:1 or 4:1 ratios requires ends of members by blocking, bridging, hangers to have cl=1.0. typically the number of trimmer and cripple studs are selected by the span and provide this support. additionally the interior and exterior sheathing provides additional support. for height:thickness to assume cl=1.0 2:1 and less case, no supports are required 3:1 or 4:1 case, at ends of members by blocking, bridging, hangers. 5:1 case, then the lateral stability requirements are: a. the compression edge is held in-line the entire beam length b. the member ends are held in position with full depth blocking, hangers, or bridging. beam stability factor equation: cl=((1+q/1.9)-((1+q/1.9)**2-q/0.95)**1/2)</= 1.0 g=fbe/fb* fbe=(kbe/ey'/rb)**2 kbe= 0.438 lumber, graded 0.610 glulamms ey'=ey(cm)cl |